Hi,
Hopefully you guys have some ideas about what's going on because I'm hoping we can get to the bottom of this problem sooner than later.
So, here is the skinny:
We have a 5KV "transmission" circuit that we are unable to energize.
Background and story: the purpose of the circuit is to span about 1500ft with minimal line loss/vdrop out to a PV array. The circuit is comprised of a 1MVA 480v wye primary to 4.8kv delta secondary, 1500ft of 500kcmil AL 5kv rated conductor, then terminating in a 4800v primary, 480 secondary 1MVA transformer.
The first test of the circuit failed with the breaker holding about a minute and tripping out. Over the phone my thought was an issue with cascading transformers (possibly inrush or zero crossing) so we tested lifting the mv conductor and seeing if we could energize just the first transformer. This worked without an issue. Next test. We megged the lines and we definitely had a problem, turns out the installer had created a high impedance fault with a conductive layer of the conductor to the concentric shield. The initial closing in on the system had smoked the ends of the conductor so new conductor was pulled.
The new conductor megs out good, but everything has been cautious in testing here because its not a cheap mistake to fault out another pull. Tested first xfmr alone and it powers up. Tested transformer with conductor attached ( floating on opposite end and not attached to the transformer) and it trips out instantly. Again megging phase to phase and phase to shield tests out OK. An instant trip to me would seem to indicate the GFCI is tripping vs. Current overload.
The transformer has it's own GEC and both the 480v and 4.8kv equipment (including the shield conductors) all come to a common ground bus in the transformer and the 480V EGC also goes back to the service GEC. Not quite as designed but it's where we are currently.
I have thoughts about the issue and put together some procedures for testing but I wanted to see if anyone else has any ideas without the bias of what I am already trying.
Thoughts/questions?
Thoughts/questions?