Just want to run this past those smarter than myself.   Concrete floor, masonry wall cabin with 100 amp service. FPE main panel,  No ground rods.  Initially I looked and thought the can was bonded but after a shock last night I quit working and came back and did a thorough service investigation this morning.  Surprise neutral was floating.  One branch ckt neutral was landed on a ground bar.  I added a 4 wire sub panel neutral ground separation.  It looked initially like there was a bonding screw on the neutral bar so I went about my business as if things were okay.  EMT between panels.  Last night I was running EMT and was kneeling on the concrete (wet) when I got shocked.  Today I am adding ground rods new feeder and new main panel.  I believe this will clear up the problem.  Am I missing anything.  I assume I got shocked because my body was a better return path than my subpanel pipe and ground which was tied to the neutral.  I know my pipe and ground gave me a false reading to the can from the floating neutral bar this morning.  Hope this makes sense.
	
		
			
		
		
	
				
			
				
			