Thanks Bob,
Would a shorted capacitor have a very low or Zero value?
Would a shorted capacitor have a very low or Zero value?
Typically, a bad Cap will be open, not shorted.ramsy said:Thanks Bob,
Would a shorted capacitor have a very low or Zero value?
ramsy said:Thanks Bob,
Would a shorted capacitor have a very low or Zero value?
PetrosA said:Lots of good info here for sure!
Fishin, I'm still not sure what FOP means here...
Short cycling could be the issue, but I think that should be up to the AC guy to check, as should a recording meter.
Meggering - I spoke to my boss about getting hold of one (he doesn't have one) so I can check the feeds up to the disconnect and into the unit. We'll see if he can handle that request
John, unfortunately, it's got a printed (not enameled or stamped) nameplate. I'm guessing the unit is at least 25-30 years old and nothing is legible on the nameplate anymore. It's being fed with #8 CU and the run can't be more than 50' or so, so I don't think Vdrop is the issue.
My wife's getting more and more ready to go into labor, but if it doesn't happen over the weekend, I'll probably be back there Monday or Tuesday and I'll be able to give some more info then.
Thanks for all your ideas!
That's a good idea, but it's more of a new install issue. It sounds like this has been in place and working for a few years now, so I doubt it's just starting to become a problem.john m. caloggero said:Hello Peter, Unfortunately you have not provided the nameplate data of the air cond, such as full load amps and voltage. But assume that the FLA is 16amps, at 230V.
Refrigerant motor compressors are covered in Art 440. The mfgs information provides the minimum conductor size and the maximum ground-fault short-circuit protection. Assuming that the nameplate rated load current is 16 amperes, the circuit breaker could be rated 175 % of that or 1.75 x 16A = 28A, therefore a 30A CB is allowed. However, that is if the proper voltage is available at the compressor location. If the branch-circuit is a rather long, a voltage drop will cause the compressor to draw more current and trip the breaker.
If this is the cause, larger gauge conductors will have to be installed to minimize voltage drop. In addition, Sect 440-22 of the 2005 NEC allows the Breaker to be increased to 225 % of the rated load. However, it cannot exceed the branch-circuit selection current.
DanZ said:It sounds like this has been in place and working for a few years now..
You know, that sounds like a better idea! Maybe you can rent Mark or Brian to come over and do it...and teach you how at the same time! :grin:ptonsparky said:If you are absolutely sure you will not use one more than once or twice a year, rent one with the electrician attached to it and watch, then buy one. You will use it.
electricalperson said:make sure you dont megger line to line. ..or a good capacitor will suddenly become a bad capacitor. ..if its 120 lets say set the megger for 250. 240 volt set the megger to 500 and so on
Minuteman said:Typically, a bad Cap will be open, not shorted.