zeero3
Member
- Location
- San Francisco, California, USA
120/240V Single Phase Service (Residence)
GE Panel with 16 breaker slots and 90A main located at meter bank outside
(Top 4 breakers on line A, next 4 breakers on line B, etc)
Guessing residence (condo) was built in the 1970s
Raceways are conduit or flex (no romex).
No ground wires.
Issue:
Line A goes down when a line to neutral circuit on line A is used (issue does not consistently recreate)
What I mean by this is that if a light (that is on a line A circuit) is turned on, the issue may occur, though is random.
According to what I've seen, line A has never went down when a line B circuit was used.
Line A has also never went down when a 240V circuit was energized (they have 2 240V electric heaters and a 240 range).
KICKER:
When line A is down, turning the 240V electric heater ON brings line A back up. Can shut the 240V heater off immediately after and line A stays back up until it goes down again by turning on a light on line A. Also, no breakers ever trip and I've yet to see any frayed or burnt wires anywhere.
What I've done so far:
Guts were loose in the panel so I cleaned the panel. This consisted of making sure to bolt guts down properly. Checking the bus for oxidation or anything out of the ordinary. Checked each breaker. Reattached lines A and B and neutral. Reconnected and labeled all branch circuits. Removed an illegal bonding jumper from panel to neutral bar. Removed all neutrals from the neutral bar and tested to make sure all branch circuits were independent of each other. Made sure all neutral were independent of each other and not improperly tied together downstream. Labeled neutrals and reconnected to neutral bar. Checked for any other objectionable current paths by testing continuity between branch HR neutrals to outgoing conduit it is run in (only one found was for the 240V range). Capped both 240V heater circuits at the heaters and shut off both of their two pole breakers. (Thought there might be an issue at the heater's wiring due to age and temperature changes so I eliminated this to find out, now their hack solution to bringing the A line back up is moot.)
My thoughts:
Utility company came out and everything is fine up to the meter. First thought was that it was the main breaker, but every time I have a guess at something upstream of the panel, I keep saying "but how would turning on the 240V heater bring line A back up?" I didn't find a neutral that needed to be separated (I initially was thinking this was the issue). I'm a little bit stumped and frustrated and I've talked to a few other electricians at work. Has anyone heard of something similar? A line A light (dining room or kitchen) seems to be the most common culprit so my next step is to replace the switch. Loose connections at the main sound reasonable as well, but not when I remember about the 240V heater bringing line A back up. When everything is up line-to-neutral (both lines) is 123V and line-to-line is about 213V.
I know this is a lot, but I wanted to give as much information as I could to see if this rings a bell for anyone. Thanks in advance to anyone that has a lead.....
GE Panel with 16 breaker slots and 90A main located at meter bank outside
(Top 4 breakers on line A, next 4 breakers on line B, etc)
Guessing residence (condo) was built in the 1970s
Raceways are conduit or flex (no romex).
No ground wires.
Issue:
Line A goes down when a line to neutral circuit on line A is used (issue does not consistently recreate)
What I mean by this is that if a light (that is on a line A circuit) is turned on, the issue may occur, though is random.
According to what I've seen, line A has never went down when a line B circuit was used.
Line A has also never went down when a 240V circuit was energized (they have 2 240V electric heaters and a 240 range).
KICKER:
When line A is down, turning the 240V electric heater ON brings line A back up. Can shut the 240V heater off immediately after and line A stays back up until it goes down again by turning on a light on line A. Also, no breakers ever trip and I've yet to see any frayed or burnt wires anywhere.
What I've done so far:
Guts were loose in the panel so I cleaned the panel. This consisted of making sure to bolt guts down properly. Checking the bus for oxidation or anything out of the ordinary. Checked each breaker. Reattached lines A and B and neutral. Reconnected and labeled all branch circuits. Removed an illegal bonding jumper from panel to neutral bar. Removed all neutrals from the neutral bar and tested to make sure all branch circuits were independent of each other. Made sure all neutral were independent of each other and not improperly tied together downstream. Labeled neutrals and reconnected to neutral bar. Checked for any other objectionable current paths by testing continuity between branch HR neutrals to outgoing conduit it is run in (only one found was for the 240V range). Capped both 240V heater circuits at the heaters and shut off both of their two pole breakers. (Thought there might be an issue at the heater's wiring due to age and temperature changes so I eliminated this to find out, now their hack solution to bringing the A line back up is moot.)
My thoughts:
Utility company came out and everything is fine up to the meter. First thought was that it was the main breaker, but every time I have a guess at something upstream of the panel, I keep saying "but how would turning on the 240V heater bring line A back up?" I didn't find a neutral that needed to be separated (I initially was thinking this was the issue). I'm a little bit stumped and frustrated and I've talked to a few other electricians at work. Has anyone heard of something similar? A line A light (dining room or kitchen) seems to be the most common culprit so my next step is to replace the switch. Loose connections at the main sound reasonable as well, but not when I remember about the 240V heater bringing line A back up. When everything is up line-to-neutral (both lines) is 123V and line-to-line is about 213V.
I know this is a lot, but I wanted to give as much information as I could to see if this rings a bell for anyone. Thanks in advance to anyone that has a lead.....