dimbulb
New member
- Ruffs Dale, PA USA
The following problem has recently surfaced and has me scratching my head. This 20A circuit utilizes 12-2 romex, has two 70W dusk to dawn lamps and a liftmaster garage door opener. It is fed from a 20A Siemens single pole breaker located within a 200A sub-panel. With exception of one short segment, all romex is visible (but undamaged). This circuit has functioned as intended since 2003, up until a week ago.
The breaker only trips when the dusk to dawn lamps are active, but it can immediately be reset and may remain live for 1 to 24 hours before tripping again. I unplugged the door operator and switched off one light, and the breaker eventually tripped. Switched off that lamp and turned the other on. Again, the breaker eventually tripped. Tried a spare breaker with same result.
There is a junction box with three outputs from the panel feed -a branch for one lamp, a branch with the second lamp and the door operator, and a third branch leading about 75' to an outdoor receptacle and another indoor receptacle. Isolating the three and connecting each in turn, the longer run ONLY shows +/- 130ma with my Fluke inserted between the breaker and the feed, and the breaker on. Also, a test lamp glows when connected instead of the meter. Disconnecting the neutral gives the same result.
I found nothing abnormal inside any boxes, and no damaged insulation anywhere. With all the receptacles removed from the longer branch, Fluke readings don't change.
What am I missing, and what other tests do you suggest?
I have reconnected the two lamp circuits but not the longer branch and plan to monitor this evening when the lamps come on.