Hi, I was wondering what you guys and gals think the problem is. Plug in my plug tester, it says no neutral. Use a volt tester H-N 120V. N-G 14V. Is my plug tester broke? Should there be 14v. N-G? Thank you for your help.
Is it a MWBC? You could have be reading the unbalanced load. I don't always trust those plug in testers, sometimes they say something, but it's really something else. Like it will tell you that you have an open neutral, but it's really an open gournd.
Thank you. So between a $8 plug tester or a $200 ampprobe I think I'll trust the ampprobe.
I agree, I wouldn't be to quick to condem the $8 tester, but I also wouldn't spend all of my time looking for something that may not be the problem.
Zap, this is a case where I'd try a voltmeter in parallel with, say, a 100w bulb. Measure again, and between all three pairs.
I'm not sure what kind of meter you used. Is this a single circuit? Check at the panel end to see if the neutral is shared.
http://us.fluke.com/usen/Products/Fluke+TPRO+T.htmWouldn't it be nice to have a solenoid tester with a digital readout?
They may exist, but I haven't seen one.
It's very important for a troubleshooter to know the difference between voltage readings with or without a load.
It's also very important to know how your test equipment works. I literally know mine inside and out.
Have you ever taken a crank megger apart? They are fascinating.
I also build much of my own test equipment and I own some odd pieces as well. How many of you have a mhometer or a Geiger counter in your mess....I mean mass of gear?
Hi, I was wondering what you guys and gals think the problem is. Plug in my plug tester, it says no neutral. Use a volt tester H-N 120V. N-G 14V. Is my plug tester broke? Should there be 14v. N-G? Thank you for your help.
100209-2012 EST
zappy:
I believe I mentioned to you before that you need to find some good reference material, books, on electrical circuit theory, and then study and play with different circuits.
Your current problem. String a wire from a screwdriver in the earth outside. From this reference measure the voltage to various places with a high impedance meter. To hot lines anywhere your voltage reading should be within a few volts (on heavily loaded circuits maybe not more than 5 V) difference from the line to neutral voltage in the main panel. Same on any neutral. Light loads much closer to 0 V difference. On EGC the voltage to outside earth should not be very dependent on loads and probably should be less than 1 V as a rough criteria. Also voltage from the earth probe to main panel neutral-EGC point should be a fraction of a volt, if not investigate problems in this area.
Suppose you get an EGC reading of 14 V or maybe 40 or 60 V, then likely the EGC is not connected to neutral at the panel and to earth. Put some load across your meter terminals, maybe the referenced 100 W bulb by Larry (about 10 ohms with little voltage across the bulb) .With this load and with a floating EGC the voltage should drop to near 0.
Now suppose the EGC is good. Based on not reading a phantom voltage. Then use your ohmmeter to measure resistance from the EGC to neutral at the main panel. If near 0 ohms, then connect a test 100 W bulb from a hot line somewhere to your EGC and measure the voltage of the EGC back to your earth reference. If this voltage is low, probably a fraction of a volt, then you have a good preliminary indication of a good EGC.
If you know the EGC is good and you read 14 V to neutral, then there is a neutral problem. This problem voltage should vary substantially with loading. Now you search for the problem.
.
He probably did not want to bill himself. :grin:I'll write down what I found, and you can send him the bill! He didn't want to bother.
He probably did not want to bill himself. :grin:
100210-0814 EST
Zappy:
I am hoping to give you some concepts that can assist your troublehooting.
I differ from others in that I suggest using a high impedance high resolution voltmeter, and when necessary adding in parallel a much lower impedance for some tests. This may be little more awkward than just using a Wiggy, but with an accurate high resolution meter I can get information that you can not get with a Wiggy.
Small voltage drop measurements can be a very important troubleshooting tool. For normal 120 to 240 volt circuits this means resolving 0.1 V (100 MV) when on a range that reads 240 V. A #12 copper wire has a 20 deg C resistance of about 1.6 ohms/1000 ft. When a wire is not heated from a heavy load, then the 20 deg C (68 deg F) is a valid temperature to use. So 1 foot of #12 is 0.0016 ohms. A 10 A current thru this 1 ft length produces 16 MV drop, and 10 ft 160 MV. A typical DVM (digital voltmeter) that can resolve 0.1 V at 240 will also have a millivolt range that can resolve 0.1 MV.
Let's start at a center tapped pole transformer. If we can get a meter lead connected to that center tap point we can get a lot of troubleshooting information. How can we do this? This center tap will always be connected to a ground rod at the transformer. If we assume that the connections from the center tap to the ground rod are good and very little current flows thru this ground rod, then a connection of our meter lead to the wire to the ground rod is very close to being directly on the center tap point.
Using similar assumptions the neutral wire from the transformer to the main panel can also be considered to be equivalent to the transformer center tap if no current is flowing in the neutral. Or if current is flowing in the neutral, then the assumption is modified by the phase and voltage drop along the neutral.
For the present I will stop here and ask if this is clear to you?
.
Hi, I was wondering what you guys and gals think the problem is. Plug in my plug tester, it says no neutral. Use a volt tester H-N 120V. N-G 14V. Is my plug tester broke? Should there be 14v. N-G? Thank you for your help.