Yes, 10 amperes thru #12 copper wire will produce about 16 MV drop across any 1 foot section you want to measure.
Make two test probes with a 3 prong plug on each. Connect the test lead wire, I use Belden 8521 stranded #16 because I have lots of this in stock, to the neutral pin in the plug. These might be 6 ft long. Get some banana plugs or just use your normal clip leads to connect to these probe wires.To extend one use a standard extension cord.
Find two outlets on the same circuit where you can guesstimate the wire size and length. Connect your meter to the two outlets thru these leads.
With no load on that circuit your meter reading should be close to 0.0 MV. Now plug a 1500 W heater into the other half of one of the outlets. Does the meter reading change by very much? If not the heater is on the source side of the two outlets. Now move the heater load to the other outlet. If the previous assumption was the case, then this voltage will be much larger and if you do not measure the current to the heater assume it is 12 A. Then calculate your wire length.
If the length seems excessively long, then you might have some bad connections. Use 0.0016 ohms per foot for #12 copper and for #14 use 0.0025 ohms/ft. If you want the values for aluminum look up the ratio of aluminum to copper.
I also have plugs with the hot brought out, and others with the EGC. Finally one plug with hot and neutral brought to a dual banana plug, another with hot and EGC, and last neutral and EGC.
All these plug cable assemblies need to be properly labeled or color coded.
You may want to use shrouded banana plugs.
.
zappy:
Yes, 10 amperes thru #12 copper wire will produce about 16 MV drop across any 1 foot section you want to measure.
Make two test probes with a 3 prong plug on each. Connect the test lead wire, I use Belden 8521 stranded #16 because I have lots of this in stock, to the neutral pin in the plug. These might be 6 ft long. Get some banana plugs or just use your normal clip leads to connect to these probe wires.To extend one use a standard extension cord.
Find two outlets on the same circuit where you can guesstimate the wire size and length. Connect your meter to the two outlets thru these leads.
With no load on that circuit your meter reading should be close to 0.0 MV. Now plug a 1500 W heater into the other half of one of the outlets. Does the meter reading change by very much? If not the heater is on the source side of the two outlets. Now move the heater load to the other outlet. If the previous assumption was the case, then this voltage will be much larger and if you do not measure the current to the heater assume it is 12 A. Then calculate your wire length.
If the length seems excessively long, then you might have some bad connections. Use 0.0016 ohms per foot for #12 copper and for #14 use 0.0025 ohms/ft. If you want the values for aluminum look up the ratio of aluminum to copper.
I also have plugs with the hot brought out, and others with the EGC. Finally one plug with hot and neutral brought to a dual banana plug, another with hot and EGC, and last neutral and EGC.
All these plug cable assemblies need to be properly labeled or color coded.
You may want to use shrouded banana plugs.
.