More likely for said nick to develop into a bigger problem over time.
Yes, that was what I was getting at, if the insulation on the aluminum was nicked, I was thinking water and the elements could slowly corrode it to the point it couldn't handle a large load, but may work fine under a light load. But I was only speculating, I really don't have any real world experience with this potential scenario.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Yes, that was what I was getting at, if the insulation on the aluminum was nicked, I was thinking water and the elements could slowly corrode it to the point it couldn't handle a large load, but may work fine under a light load.
That's what happens with every compromised- or open-neutral condition: the voltage imbalance is dependent on the current imbalance.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Yes, that was what I was getting at, if the insulation on the aluminum was nicked, I was thinking water and the elements could slowly corrode it to the point it couldn't handle a large load, but may work fine under a light load. But I was only speculating, I really don't have any real world experience with this potential scenario.
Seems to be much bigger issue with underground than with overhead wiring.

POCO's have bare aluminum ACSR for primary conductors and those take the elements as well as an ACSR bare grounded conductor on secondary lines. Connections need special attention but just exposing the conductor doesn't cause much for trouble as long as it remains in free air.
 

Sea Nile

Senior Member
Location
Georgia
Occupation
Electrician
Seems to be much bigger issue with underground than with overhead wiring.

POCO's have bare aluminum ACSR for primary conductors and those take the elements as well as an ACSR bare grounded conductor on secondary lines. Connections need special attention but just exposing the conductor doesn't cause much for trouble as long as it remains in free air.

I agree with you, in fact the OP never said if it was a drop or a lateral. I was thinking service lateral in all my comments
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
I agree with you, in fact the OP never said if it was a drop or a lateral. I was thinking service lateral in all my comments
I've been finding and fixing underground faults for 35ish years. Other than when physical abuse happened such as excavating equipment hits a line or they drive a steel post into it, copper almost never has much problems, aluminum however oxidizes away until there is nothing left. You bad spot on aluminum is usually pretty obvious once you uncover the conductor, will be nothing but aluminum oxide where there once was aluminum.

My best guess is it starts deteriorating at the damaged spot in the insulation, keeps eating away at the conductor lessening the cross section at that area. Essentially making that spot a lot like a fuse link. As you add load it operates a little warmer, which also probably helps speed up oxidation at same time.

Can't say I ever run into situation where there is reduced volts because of resistance though. That "fuse link" still has relatively low resistance just can't carry as much current as the full sized conductor but has little linear length to it so not like reducing a 4/0 to a #10 for several feet, we just talking inches most the time which is no different than placing a fuse link in the circuit. These usually fail with no warning just like a fuse link would when it opens.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I've been finding and fixing underground faults for 35ish years. Other than when physical abuse happened such as excavating equipment hits a line or they drive a steel post into it, copper almost never has much problems, aluminum however oxidizes away until there is nothing left. You bad spot on aluminum is usually pretty obvious once you uncover the conductor, will be nothing but aluminum oxide where there once was aluminum.

My best guess is it starts deteriorating at the damaged spot in the insulation, keeps eating away at the conductor lessening the cross section at that area. Essentially making that spot a lot like a fuse link. As you add load it operates a little warmer, which also probably helps speed up oxidation at same time.

Can't say I ever run into situation where there is reduced volts because of resistance though. That "fuse link" still has relatively low resistance just can't carry as much current as the full sized conductor but has little linear length to it so not like reducing a 4/0 to a #10 for several feet, we just talking inches most the time which is no different than placing a fuse link in the circuit. These usually fail with no warning just like a fuse link would when it opens.
Fertilizer seems to eat aluminum up, I used cast aluminum bell boxes for driveway lights at a gas station, they were constantly spraying fertilizer on the grass, and after a couple of years, the boxes were basically dust! LOL! Probably what oxidizes the aluminum underground when it gets nicked.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
You may have some low voltage with no load that drops again when you load it up.
When that happens the conductor basically has already deteriorated all the way through, usually won't carry any significant load at all though. LED lights, those might work to some extent as long as total load is no more than maybe 50-100 mA.
 

meternerd

Senior Member
Location
Athol, ID
Occupation
retired water & electric utility electrician, meter/relay tech
I think there is a particular model or product line with that name.
If anyone really cares.....just search for "electric beast of burden." It is a great tool to allow testing of services by utility meter techs before you call out a line crew.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Usually power company issue. Have them check their connection
Bad advice to call poco without doing due diligence while your there.
I have made many electricians look bad to customers because they called the POCO and didn't look quite far enough.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Bad advice to call poco without doing due diligence while your there.
I have made many electricians look bad to customers because they called the POCO and didn't look quite far enough.
I agree, do not call them until you know the problem is on their side and/or you cannot do further testing without disconnect.
Then be there when they are.
A hand held hair dryer or milk house heater is all you need for load unless you want to see the connection smoke.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Bad advice to call poco without doing due diligence while your there.
I have made many electricians look bad to customers because they called the POCO and didn't look quite far enough.
I agree, check everything before you call.
But on the same token, I have made a few lineman look bad, when they have said nothing was wrong on their end when a customer had called them before me. When I show them the problem is beyond the customer side. That's usually because they only "looked" at a weatherhead connection, or transformer connection from the ground. When I showed them the measurements I took and where, they then will dig deeper and find it's one of their connections.
 