If this is 208 or 240 volts and you have three single phase heaters rated 240 volts just connect one between each output terminal (resulting in a delta configuration of the output loads). Total current at full voltage will be 240 (or 208) divided by 1.73.
If you have 120 volt heaters connect them in a wye configuration instead. One lead of each heater to an output lead of your starter and other leads all three tie together (the mid point of the wye) but do not ground this point. Each heater will see 120 volts if the input is 208, but will be higher if input is 240 - about 138 volts.
This is no different than connecting transformer or motor windings in same configurations.
Well, I don't have three 240 volt heaters laying around and I'm not in the greaest position to go out and buy them This is interesting and an approach I haven't taken before so just so I understand correctly... If I did have three 240 heaters I could put an equal amount of resistance on the drive by putting for example heater 1 on A and B, heater 2 on B and C, heater 3 on A and C?