Well I just spoke with the EC. I ask if he would megger the line. He said they don't own that expensive testing device. (I don't have one either, but then again I don't do electrical day in and out). He tapped danced around the used breaker and said his guy would be outh there later this morning.
It is kinda fun not being the one in the crosshairs for a change
c2500
Find another electrician.
It does sound as if the situation is such that the problem can be isolated with a Wiggy, but his response doesn't exactly instill confidence.
On another note, continually resetting the CB accomplishes nothing but to confirm what we already know...that there is a problem.
Use test equipment to isolate and repair the problem, then reset the CB.
I guess if you reset the CB enough times it will burn the fault clear or the CB will fail/blow-up (believe me, this can happen) and the problem still exists.