I have numerous conduits entering the electrical room that are going to numerous panels in the room, approx. 200 ccc's. Some conduits have ccc's that go to more than one panel so a 12x12 trough was installed over the panels. The field conduits enter the trough and the ccc's split into their designated panels. Each panel has sufficent number of nipples to the trough. All 20 amp circuits using #10 wire because of the field conduit fill derating. I have never had a inspection failure doing this and have seen 100's of similar installs. My PM insists that we must use the 366.22 (a) making the trough non compliant because of the well over 30 ccc's in the trough. Let me note that most of the ccc's pass directly into the panel below while other ccc's are diverted in the trough to their respected panels. My question is if this is the case then why have I not had a failure before and why is this method so common with these installs. Thanks.