- Location
- Massachusetts
What if the wireway is 12X12X12?
Less than 24" no derating needed or use 310.15(A)(2)
What if the wireway is 12X12X12?
+1 :thumbsup:In my opinion, that exception applies anywhere you are required to adjust or correct a conductor's ampacity.
FIFY....If you were to slide a paper thin razor in a vertical cross section (with power off ) Would it cut through 31 wires or more? Simple as that.
Ditto....
It is not explicitly stated, but most analysis I have seen assumes that the cross section is perpendicular to the long dimension of the trough.
Requiring all cross sections (horizontal, vertical, front to back) to meet the 30 conductor limit seems pointless.
Less than 24" no derating needed
8-136 Log #2581 NEC-P08 Final Action: Reject
(376.22(B))
________________________________________________________________
Submitter: Paul E. Guidry, Fluor Enterprises, Inc.
Recommendation: Add new text to read as follows:
The adjustment factors in 310.15(B)(3)(A) shall not apply to wireways not
exceeding 0.6m (24 in) in length.
Substantiation: This would be the same conditions and rules currently found
in the Code for conduit nipples. There isn’t any difference between a conduit
nipple and a short length of wireway.
Panel Meeting Action: Reject
Panel Statement: See panel statement on Proposal 8-135.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
IMO that doesn't apply to wireways.