B brianthejabroni2 Member Yesterday at 4:09 PM #1 I am having trouble sizing a trough/wireway. Would the attached sketch be code compliant? Is sizing wireway same as sizing box? Attachments IMG_1496.jpeg 903.9 KB · Views: 13
I am having trouble sizing a trough/wireway. Would the attached sketch be code compliant? Is sizing wireway same as sizing box?
JoeStillman Senior Member Location West Chester, PA Occupation Electrical PE Yesterday at 4:59 PM #2 NEC article 376 covers wireways. You can size the wireway based on the number and size of the conductors in it, not the conduit. See 376.22. But also, if you are using it as a pull box, you size it like a box. See 376.23.