Isolated ground receptacles installed in nonmetallic boxes must be covered with a nonmetallic faceplate because a metal faceplate cannot be grounded to the circuit equipment grounding conductor.

True or False?

The answer is given as True, but I answered False because of the "must" in the statement. I understand the exception to 406.2(D)(2) to mean we can use a metallic cover if the box contains a way to ground the faceplate. What do you all think?

Bobby
 

Shockedby277v

Senior Member
Location
Michigan
"because a metal faceplate cannot be grounded to the circuit equipment grounding conductor."

I would answer true. The way I'm reading 406.2 (D)2 along with the exception , is that a metal faceplate may be used IF it has a path to the ground.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It's true. The metal faceplate is required to be grounded. This is not possible with an IG in a plastic box.
 