Isolated ground receptacles installed in nonmetallic boxes must be covered with a nonmetallic faceplate because a metal faceplate cannot be grounded to the circuit equipment grounding conductor.
True or False?
The answer is given as True, but I answered False because of the "must" in the statement. I understand the exception to 406.2(D)(2) to mean we can use a metallic cover if the box contains a way to ground the faceplate. What do you all think?
Bobby