BEWARE of relying too much on those "true" RMS measurements in certain circumstances.
Case in point: Recently we were troubleshooting some magnetic contacts that hold fire stop doors open at an auditorium. There were some doors that would not stay open on the magnets --- they seemed to be a bit weak.
Taking voltage measurements with a Fluke true RMS meter showed something around 50+ volts or so -- way more than the 24 Volts that was supposed to be present.
Using a different meter showed 26 Volts, just about right for such an installation.
Something in the power supply transformer or other circuitry was giving off those false readings using the so-called "true" RMS values.
So, before you take everything apart, use sound judgement and check things with more than one meter, if necessary.
FWIW, we replaced those "weak" magnets with new ones, and have not had any more problems with them.