I am working on a tenant improvement project with a 240/120V, 3 Phase system. I assumed this was a high-leg delta system. Existing panels in the building had markers on them that say "HI LEG PHASE B". There is a main disconnect in the electrical room through which power enters. The disconnect is labeled 400 amps. Today we opened up the disconnect and noticed that there are 400A fuses on two legs of the service and a third 200A fuse.
I am now confused as to what my electrical capacity is. I had assumed I had 240V * sqrt(3) * 400 = 166.4 KVA
Now knowing that what I assume the B phase is fused at 200A, am I right to assume my capacity now is:
400A * 120V = 48KVA+
400A * 120V = 48KVA+
200A * 120V = 24KVA
120KVA
Additionally, I also think I am limited to a maximum of 96KVA for my single phase 240V or 120V loads.
And just 83.1KVA for my three phase loads.
But in total the loads cannot exceed 120KVA.
Are my assumptions correct? Am I using the right formulas to calculate capacity on such a system?