081209-2008 EST
The NEC statements quoted by Pierre I believe mean the following:
(1) You must have a dedicated conductor(s), called an ECG, running from every piece of equipment back to a central common bus at the service entrance.
(2) You can not use the building steel structure in place of said dedicated conductor.
This does not say that the building structure can not be tied to this same common bus at the service entrance. It does not say that the building structure can not carry fault current. It does not say how much fault current is allowed to flow thru the building structure.
It is quite possible that if the building I beams are welded together that this will provide a much lower resistance path for fault currents than the required EGC. It will also provide much lower resistance between machines and thus likely less noise voltage between machines than would the required EGC. But this does not mean it can be used as the required EGC.
Building steel may not be a reliable ECG path in comparison with a known continuous length of copper wire of an adequate size, and generally in a protected enclosed path. This is because building steel is intended for structural purposes, is made of many small pieces and corresponding joints, and there are no specifications on how to build this structure as a guaranteed low impedance path. It might be good and it might not.
.