I am running home-runs for a commercial building, and I am thinking it will be easier to run multiwire branch circuits.
I plan on running 3/4 fmc from panel to12”x12” x6” j box in the ceiling. Each Fmc will contain 3 multi wire branch circuits. 6 circuits total.
I plan on using 2 pole 20 amp circuit breakers for each multi wire branch circuit. Each mwbc will contain two ungrounded conductors and one grounded giving me a total of 10 #12 conductors in each 3/4” fmc raceway.
They should have a 21a correction factor after adjustment factors.
As I understand it, as long as each each mwbc is protected by a 20 amp circuit breaker, and fed from A and B phase, the current on the neutral Should not exceed 20 amps.
Example
Circuit 5 has a load of 10 amps and circuit 7 has a load of 8 amps. The neutral conductor will have an ampacity of 2 amps.
Am I understanding this correctly, or no?
Do the loads have to be balanced?
Picture is exaample of how the circuits will be fed from circuit breaker, what the circuit is providing power to, and each raceway for mwbc’s
Again I appreciate all the help in advance!
I plan on running 3/4 fmc from panel to12”x12” x6” j box in the ceiling. Each Fmc will contain 3 multi wire branch circuits. 6 circuits total.
I plan on using 2 pole 20 amp circuit breakers for each multi wire branch circuit. Each mwbc will contain two ungrounded conductors and one grounded giving me a total of 10 #12 conductors in each 3/4” fmc raceway.
They should have a 21a correction factor after adjustment factors.
As I understand it, as long as each each mwbc is protected by a 20 amp circuit breaker, and fed from A and B phase, the current on the neutral Should not exceed 20 amps.
Example
Circuit 5 has a load of 10 amps and circuit 7 has a load of 8 amps. The neutral conductor will have an ampacity of 2 amps.
Am I understanding this correctly, or no?
Do the loads have to be balanced?
Picture is exaample of how the circuits will be fed from circuit breaker, what the circuit is providing power to, and each raceway for mwbc’s
Again I appreciate all the help in advance!