Trying to understand multiwire branch circuits

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No. It's "a" (singular) multiwire branch "circuit" (singular)
It's still 2 circuits. If I need two individual branch circuits for the kitchen counter receptacles and I run one 3-wire MWBC to feed the receptacles I have run two circuits (not one) and I have complied with the minimum number of two SABC's being required. It can be considered a single circuits for other sections of the NEC.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The NEC let's us consider it as two but it is a single circuit.

210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall
be permitted as multiwire circuits. A multiwire circuit shall be
permitted to be considered as multiple circuits. .
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
How are you supposed to keep track of those neutrals in MWC ?
See my PI's.
 

Attachments

  • NATIONAL ELECTRIC CODE 2023 - Section 200.4(C) Proposed Amendment.jpg
    NATIONAL ELECTRIC CODE 2023 - Section 200.4(C) Proposed Amendment.jpg
    287.2 KB · Views: 12
  • NATIONAL ELECTRIC CODE 2023 - Section 200.6(A) Proposed Amendment.jpg
    NATIONAL ELECTRIC CODE 2023 - Section 200.6(A) Proposed Amendment.jpg
    452.3 KB · Views: 11

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How are you supposed to keep track of those neutrals in MWC ?
If they're in a cable you do nothing. In a raceway you just wrap a number tag around them or tie them together with the ungrounded conductors. I know that you've been pushing to get this continuous stripe thing into the code but IMO with the way the CMP's have been leaning lately it's not likely to make it.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Sometimes, it's not a good idea !
 

Attachments

  • Electrical Wiring Residential - Multiwire.jpg
    Electrical Wiring Residential - Multiwire.jpg
    380.7 KB · Views: 22