Do I need to provide a TVSS on the load side of the step down transformer if I have a TVSS installed in the main switchboard?
 

StephenSDH

Senior Member
Location
Allentown, PA
The TVSS on the primary will also protect the secondary side if the voltage transient originates from the primary (aka utility).

If there is a voltage transient originating on the secondary then the TVSS on the primary will not provide much protection, because of the impedance of the transformer.

Generally the TVSS are only located primary as close as possible to the incoming utility lines.
 