Trouyano said:when their is no more room in a panel and you want to add more circuits, is their anything in the nec that prohibits use of twins or the amount of twins you can add as long as the panel is not being overloaded? Or should you add a sub panel and add circuits?
sparky_magoo said:The panel usually sez how many ckt.'s are allowed. This number is usually twice the number of spaces allowed.
Yes their are tandem QO's. The only problem with adding tandems is the load now going to exceed your neutral rating?360Youth said:I would say most panels that allow twins or tandems are 30/40, but I have seen my fair share of 20/40. I thought the circuit limit was 42, not 40 and the only panel I had seen that would take more (w/o some serious modification) were the QOs. They may have changed, but their bus bar would allow a tandem anywhere on it, thus allowing 60 circuits. But i think they changed the design on the "snap bar" that the hook on the tandem breaker would only fit in specifed spots. Off topic, but does QO make a 2-pole tandem like HomeLine and other brands??
Okay, now you're gonna need to explain that one.ceb said:Yes their are tandem QO's. The only problem with adding tandems is the load now going to exceed your neutral rating?
ceb said:Yes their are tandem QO's. The only problem with adding tandems is the load now going to exceed your neutral rating?
OK Marc, give me a break I had a brain fart. I have seen a case where some one used 14-3 on a tandem as a MWBC to feed recpt. and lights in a room and then feed a new addition recp. and lights. The net. was carrying the full load not the unbalanced as a MWBC wouldmdshunk said:Okay, now you're gonna need to explain that one.