I have been having a non argument with a senior inspector over a install that I failed. a homeowner doing install wanted to have two seperate services, two adjacent service drops, meter mains next to each other. The next day he said that he went there and gave a list of corrections and the utility would connect both masts with one drop.
I see more than a few hazardous problems and said that it was not legal (99 nec, or cec). I can see legal with one set of risers, gutter, etc., but he said he had him correct the bonding and pg&e will connect it. I cannot see correct way to bond and ground this system ( one meter/main will feed granny on property, same address). One ground rod as well!!.
I won't sign for it.
Any commiseration welcome. Any thoughts as well.
any pg%e guys out there? will you connect it?
felling my sign on, paul
I see more than a few hazardous problems and said that it was not legal (99 nec, or cec). I can see legal with one set of risers, gutter, etc., but he said he had him correct the bonding and pg&e will connect it. I cannot see correct way to bond and ground this system ( one meter/main will feed granny on property, same address). One ground rod as well!!.