I have a question on temporary industrial machines that utilize 20 and 30 amp 480V 3-Phase twist lock cord and plug connections. We have multiple 30 amp receptacles located on presses within our company - properly fused at the machine for protecting the conductors supplying the receps, but the auxilliary equipment utilizes 20 Amps. I see that many of these aux. machines have (what I would call) "quick change-over" cords - or, a 30 Amp Male to a 20 Amp female short extension cord or a 30 Amp plug feeding 20 Amp flexible cord.
The department in question is not under my control but I was asked about the proper way to supply a new piece of auxilliary equipment rated at 20 Amps. So, this being the case - I had a small debate with our Master electrician this morning and we both had seemingly valid points (I am but a humble journeyman who has not been active in electrical installation for a number of years) we are both more of controls/automoation electricians who are licensed electricians and good friends - so it was a positive debate - yet still a debate.
Here were the points:
NOTE: We both agree that the best answer is to install 20 Amp receptacles on the presses.
1. Master claimed the auxilliary machine cord had to be sized for a 30 amps if using a 30 amp plug.
2. I seemed to recall (under industrial exceptions possibly?) being able to use a 30 Amp plug with 20 Amp listed flexible cord (hard-wired, not an extension cord) feeding the auxilliary unit so long as the auxilliary units supply conductors were properly protected for the load - each auxilliary unit wired in this manner has a nameplate rating of 20 Amps or less total combined load. I based my argument on the fact that other loads such as electric hand tools, fans and fluorescent lighting are done this way. Am I missing something here?
The idea being able to power the unit from provided 30 Amp receptacles yet protect the units 20 Amp conductors from SS/GF and overheating .........
Thanks for any replies
The department in question is not under my control but I was asked about the proper way to supply a new piece of auxilliary equipment rated at 20 Amps. So, this being the case - I had a small debate with our Master electrician this morning and we both had seemingly valid points (I am but a humble journeyman who has not been active in electrical installation for a number of years) we are both more of controls/automoation electricians who are licensed electricians and good friends - so it was a positive debate - yet still a debate.
Here were the points:
NOTE: We both agree that the best answer is to install 20 Amp receptacles on the presses.
1. Master claimed the auxilliary machine cord had to be sized for a 30 amps if using a 30 amp plug.
2. I seemed to recall (under industrial exceptions possibly?) being able to use a 30 Amp plug with 20 Amp listed flexible cord (hard-wired, not an extension cord) feeding the auxilliary unit so long as the auxilliary units supply conductors were properly protected for the load - each auxilliary unit wired in this manner has a nameplate rating of 20 Amps or less total combined load. I based my argument on the fact that other loads such as electric hand tools, fans and fluorescent lighting are done this way. Am I missing something here?
The idea being able to power the unit from provided 30 Amp receptacles yet protect the units 20 Amp conductors from SS/GF and overheating .........
Thanks for any replies