Can total load be discounted by dividing it by 1.732 if not feeding 3-Phase loads? 2-pole breakers feed single-phase loads.
Yes. A 3 phase circuit supplies the pdu.
Can total load be discounted by dividing it by 1.732 if not feeding 3-Phase loads? 2-pole breakers feed single-phase loads.
Can total load be discounted by dividing it by 1.732 if not feeding 3-Phase loads? 2-pole breakers feed single-phase loads.
There is no way that PDU is going to receive a UL (or other NRTL) listing. What is the 'certification' it is undergoing?
Also, I am 98.5% sure you cant have a hardwired pdu with IEC receptacles. My logic is that if its hardwired then its part of the structure and is permanently installed. Cant permanently install IEC receptacles due to their use on multiple voltages. Someone please correct me if I am wrong here.
Maybe I missed something but if you have a load of 100 amps (my hypothetical number and nothing to do with your equipment) on all three phases then that is the load on each conductor.
If instead you had a rating of 36 kVA and divided it evenly across three phases then that would still be ~100 amps but if it were 36 kVA across only two leads it jumps to 173 amps.
That 1.73 factor only applies when you are figuring the current of balanced three phase circuit when power is what is known.
This probably explains why you cannot find a "duplex" type IEC receptacle. Not sure about certification. There is a popular Crypto Beast PDU that is NRTL listed and the first line of the description is "The product covered by this report is a permanently connected, Class I, power distribution unit intended for fixing onto a shelf". It also comes with lugs for wiring.
I'm not understanding the entire discussion.
You mention that the 400 amp square D Panel can give you 100A-3Pole outputs. Why not just install (2) 100A-3Pole breakers and the associated (2) IEC 60309 pin & sleeve plugs (100A plugs) and then plug in these 100A PDU's that seem to be similar to what you want. They are already listed. https://www.raritan.com/product-sele...l/px3-4213u-v2
or this one https://www.raritan.com/product-sele...l/px2-5941v-v2
or this one https://www.raritan.com/product-sele...etail/px2-4941
183 amps of single-phase load. 3-phase is brought to the unit and then single-phase is broken out. So you get 105.7 amps on three-phase (100 amp breaker 3-phase is derated to 80 amps)..
I'm still trying to figure out where the individual protection is for the individual 120v outlets.
JAP>
Because they cost money. He's already said that.
-Hal
In another thread the OP has going, it appears cost will govern how much safety will be installed.Just buy something that will not burn the place down.
183 amps of single-phase load. 3-phase is brought to the unit and then single-phase is broken out. So you get 105.7 amps on three-phase (100 amp breaker 3-phase is derated to 80 amps)..
I guess I missed that.
What I did see in post #5 was “But we then void certifications. Fundamentally there is no issue with that, but the insurance man will probably disagree.”
so shoemaker-ing a bunch of individual components together doesn’t make an overall listed appliance.
The insurance man won’t like that. Just buy something that will not burn the place down.
The three-phase wiring input is broken out into (3) single phase 63 AMP banks (100% rated).
One thing to keep firmly in mind is that, at least for Bitcoin, the "mining" process has reached a point where the expected returns for a given block of computation is very low. A small increment in initial system cost could actually keep the operation from being profitable at all.
You know Bitcoins better than I do, but my feeling is that this is just a big waste of time by people who think they are going to strike it rich.
Then I'm just waiting for the government to crack down on it because it facilitates the exchange of untraceable funds to support illegal activities.
Now back to your regular programming...
-Hal