infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, it's even permitted to run them within the same cable. The only limitation would be if the adjacent devices were fed with a voltage above 300 volts between them. At that point the adjacent devices would require separation.
 

cadpoint

Senior Member
Location
Durham, NC
Seperation after 250 V

Seperation after 250 V

Recall'n as long as there's not more than 250 Volts total sum, then and if after that, a physical barrier is required.

Tooth slot in mud ring for Metal divider, with plastic some have a slot for the dividers some don't.
 