Yes, it's even permitted to run them within the same cable. The only limitation would be if the adjacent devices were fed with a voltage above 300 volts between them. At that point the adjacent devices would require separation.
 
Seperation after 250 V

Seperation after 250 V

Recall'n as long as there's not more than 250 Volts total sum, then and if after that, a physical barrier is required.

Tooth slot in mud ring for Metal divider, with plastic some have a slot for the dividers some don't.
 