Jerryr said:In a manufacturing facility, can you put two duplex receptacles in the same 4 x 4 box, on two different 20 amp circuits and share the common?
Dennis Alwon said:If, however, you wanted added safety you may use a dp breaker that will disconnect both hots at the same time.
Troublemaker!iwire said:How about I run three 14 AWGs (Black, Black, Green) and one 10 AWG (White) in PVC conduit to this box.
The two black 14 AWGs will be ungrounded conductors supplied from single pole breakers on phase 'A'. The green 14 will be the EGC and the white 10 AWG will be a shared neutral.
Any problems?
LarryFine said:We've hashed this out before. The multi-circuit (per phase) shared neutral is only directly addressed in outdoor festoon lighting.
roger said:BTW, in Bob's example we do not have a neutral.
Roger
LarryFine said:The multi-circuit (per phase) shared neutral is only directly addressed in outdoor festoon lighting.
LarryFine said:Troublemaker.![]()