wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
That's not at all clear to me. The definition of branch circuit makes it clear where the boundary is on the ungrounded conductor(s), but is silent on the boundary for the grounded conductor. If you see the boundary as the neutral bar, then it would be an MWBC. But perhaps the boundary is the panelboard enclosure, in which case there is no MWBC.By definition you have created MWBC so yes.
As a practical matter, if the three grounded conductors were joined to a jumper to the neutral bar with a 4-port polaris style connector rather than with a wire nut, I see no reason to consider it an MWBC. Certainly if an additional terminal bar mounted to and insulated from the enclosure were installed for the 3 grounded conductors, with a jumper to the neutral bar, it would not be an MWBC.
Cheers, Wayne