I really don't see any difference in the function of the code rules between 2008 and now. Just a different way of saying the same thing.
250.56 in the 2008 said either test and prove that your single rod meets the 25 ohm rule or install two rods. To me that is the same as what the exception to 250.53(A)(2) says in the 2014 code.
Yes, the ultimate meaning is the same but now when using a rod a second electrode required unless you can meet the exception. As Kwired pointed out prior to the 2008 it never really stated who would be providing the burden of proof.