Re: two ground rods
1999 nec
well people i appreciate all the info on the two ground rod installation. 250.50(2)requires a supplemental ground for underground water pipes. which is what i am using. ground rod #1. 250.56 say that a single electrode consisting of a rod, pipe, or plate that does NOT have a resistance to ground of 25 ohms or less, SHALL be augmented by one additional electrode of any types specified in 250.50 & 250.52. the only way to find out how much resistance is there is to test it. in the state of VA, the only people that can test them are people who are listed with the state as a certified testing agency. mega bucks for a test. so the resistance to us is unknown. therefore, in their wisdom they require us to drive two ground rods in certain areas. as long as that resistance is unknown, we have to drive a second ground rod. seems logical doesn't it? we are not required to ground the meter base, only bond it. 250.102(c)
what i was wondering is how to connect two #6, one from each disconnect, to each ground rod and still comply with 250.56.