I do mostly residential service work, so I don't do much conduit wiring. Yesterday I came to a JB that had two hots and two grounded conductors. The two hots were on different CB's. There was no marking to differentiate the grounded conductors. In looking at 200-6, conductors of different systems can have stripes on the grounded conductor.
The questions are:
1) Can grounded conductors of the same system be identified in any way, since it appears they are required to have a continuous white covering?
2) If this is permitted, what is the preferred way to do the marking in the field, or is it necessary to buy white wire with a stripe?
It seems that the neutrals of different circuits would need to be kept separate to avoid overloading the neutral, but I am confused about how to implement this.
Thanks (as always),
Mark