Re: two grounds on one rod?
Glenn,
Using a GEC from the Meter to a ground rod ( or any other Ground Electrode ) and another GEC from the Main disconnect enclosure to the same Ground Electrode (GE), ( remember all GE's are to be bonded together) those GEC's will provide a parallel path with the grounded conductor.
In general, it is difficult for Service Equipment not to have a parallel path for the grounded conductor if more than one GE or more than one GEC is used.
exactly.
As far as 250.6
"250.6 Objectionable Current over Grounding Conductors.
(A) Arrangement to Prevent Objectionable Current. The grounding of electrical systems, circuit conductors, surge arresters, and conductive non–current-carrying materials and equipment shall be
installed and arranged in a manner that will prevent objectionable current over the grounding conductors or grounding paths.
Is this talking present as in when installed, or during a fault condition?
If we're speaking present, what exactly is objectionable?
If we're talking about fault conditions that would be temporary, (no mention of how much damage must be done before it is not temporary per the NEC) grounding as many times as could be monetarily afforded upstrem of the "Main" would be legal under 250.6 (C)
Roger
[ August 18, 2003, 08:25 PM: Message edited by: roger ]