jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
...
As for current sharing, that's only an issue for 240V loads on this 120/240V system that is trying to be created, but at first glance I haven't wrapped my head around how that is going to work out. Any 120V load will be on one generator or the other.
...
Cheers, Wayne
Well, for any 240V load, physics will force the amount of current to be the same through each generator, and the question is how their control systems will react to that.
As far as 120V loads, I don't see why both generators wouldn't power the load (unless one or both inverter controls see something they don't like and cut out). One directly, the other through the transformer. The current from the 'opposite side' generator would be lower for the reasons you explained earlier. But it's not clear when this becomes a problem, which was the question from the start. The more I think about it though, I think this all means the transformer has to be rated for at least the larger generator's output. It can't just be a small transformer to provide a reference, because it will actually transfer power for unbalanced load. Right?