jesusrperezd
- California
- Engineer
Hi all, I have read several similar posts, but still have some questions. I'm exploring possible distribution schemes for a client in California, and I want to be sure the concept I have in mind is code compliant regarding transformer and conductor protection.
There are two existing switchboards, 800A and 1600A, with main breakers each, located in different buildings. The initial thought is to add a customer owned Pad Mounted transformer outside 12kV/208-120V, and provide two LV feeders from the secondary side of the transformer to each switchboard.
My interpretation is that the scheme meets the following:
NEC 240.21 (C): "A set of conductors feeding a single load, or each set of conductors feeding separate loads..." . That means that two feeders are acceptable.
240.21 (C) (4) indicates the conditions for the outside transformer; those are met.
450.3 (A) is also met: Supervised location, primary setting less than 300% (by CB and protection relay), secondary protection is not required.
An engineer said that we need to provide a switchboard downstream of the transformer with a main breaker and two branch breakers for the two switchboard feeders to comply with the code. Additionally, a post I read here mentioned that the secondary conductor is a tap, and you can't tap a tap conductor. I have been reading the code to see where the above statements are based, but found nothing. Any comment on this will be valuable. Another thing I need to verify is the correct feeder size for both switchboards.