J jesusrperezd Member Location California Occupation Engineer Jul 14, 2025 #21 Ragin Cajun said: What if there is a cable failure between the transformer and one of the panel-boards.. What will open the fault? Click to expand... The next upstream device is at the medium voltage side of the transformer
Ragin Cajun said: What if there is a cable failure between the transformer and one of the panel-boards.. What will open the fault? Click to expand... The next upstream device is at the medium voltage side of the transformer
J jesusrperezd Member Location California Occupation Engineer Jul 15, 2025 #22 infinity said: Dimming panels and stage company switches in a Broadway Theater in NYC. Click to expand... Did the size and quantity come from unbalanced load and/or harmonics?
infinity said: Dimming panels and stage company switches in a Broadway Theater in NYC. Click to expand... Did the size and quantity come from unbalanced load and/or harmonics?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Jul 16, 2025 #23 jesusrperezd said: Did the size and quantity come from unbalanced load and/or harmonics? Click to expand... The 200% neutral was for the potential of harmonics.
jesusrperezd said: Did the size and quantity come from unbalanced load and/or harmonics? Click to expand... The 200% neutral was for the potential of harmonics.