Is this setup allowed for 2 - 150amp main breaker panels and single utility meter enclosure, getting conflicting information. Single 2in sch40 conduit connection between utility enclosure and 1st panel containing (6) 2/0 Aluminum service cables. Three of these cables passes-though the 1st main breaker panel to the 2nd main breaker panel through another 2in. sch40 conduit. Each 150amp panel is wired with 2-hot, 1-neutral cable. No other cable types pass through the same service cable conduit. The feeder cables to the respective sub-panel cabinets pass through their own separate conduit. Main breaker #1 with the pass-through service cables for main breaker #2 will be labeled indicating the pass-through service cable disconnect is located in main breaker panel #2.