Thanks everyone. My limited experience with these stand alone installations is that when there is a light load, charged batteries, and the sun is shining, the voltage from the panel(s) is higher than the charging voltage which is higher than the load voltage (like 18V, 13.5V, 12.0). But when the batteries are low, and/or the load is heavy, and/or the sun isn't shining, they are all at the same voltage (like 11.8V 11.8V, 11.8V).
These panels are all about 150W, 20V max, 7.5A max. At my first visit, they just needed the radio tower working right away, and I had another time critical project also going on. Soooo... not much time to read a manual and went by hearsay about why the third panel was not connected. Replacing the controller did get things working, but can't say for certain the controller was bad, although not having the negative connected to ground may have been a problem (yes, it's connected now). Later, I posed my question to you fine folks, read the manual, and convinced the installer (who is more a boss than a co-worker...) to read the manual. He changed his mind about adding the additional panel (which I had already done as the batteries could not keep up overnight).
Sooo... got a break to go check things out when the sun was actually shining on the panels. A pretty obvious problem with panel placement as you can see from the picture. A DC clamp meter verified that the shaded panel was only putting out 1/4 the amps as the other panels. At the time the panels were 12.0V, battery 12.0V and load 12.0V. I forget the exact amps going to and from each of these, but the batteries were charging a little and the radio load was light.
Don't know if the operators or we will reposition the panel(s). Might need another panel. Not sure if a real calculation was done. On my suggestion, the operator put the batteries on a generator/charger overnight so he won't get a auto-call in the middle of the night. We'll see how things are this morning.
Thanks again, folks!
These panels are all about 150W, 20V max, 7.5A max. At my first visit, they just needed the radio tower working right away, and I had another time critical project also going on. Soooo... not much time to read a manual and went by hearsay about why the third panel was not connected. Replacing the controller did get things working, but can't say for certain the controller was bad, although not having the negative connected to ground may have been a problem (yes, it's connected now). Later, I posed my question to you fine folks, read the manual, and convinced the installer (who is more a boss than a co-worker...) to read the manual. He changed his mind about adding the additional panel (which I had already done as the batteries could not keep up overnight).
Sooo... got a break to go check things out when the sun was actually shining on the panels. A pretty obvious problem with panel placement as you can see from the picture. A DC clamp meter verified that the shaded panel was only putting out 1/4 the amps as the other panels. At the time the panels were 12.0V, battery 12.0V and load 12.0V. I forget the exact amps going to and from each of these, but the batteries were charging a little and the radio load was light.
Don't know if the operators or we will reposition the panel(s). Might need another panel. Not sure if a real calculation was done. On my suggestion, the operator put the batteries on a generator/charger overnight so he won't get a auto-call in the middle of the night. We'll see how things are this morning.
Thanks again, folks!