Davebones
Senior Member
- Location
- North Of Tampa Fl
We have custom built hydraulic test stands with various motors from 3 hp to up to 150 hp . We have started running our control power ( 120 V ) through a GFI ( For Safety as oil and water sometimes leaks around stand )then it goes thru a lockable switch next to the controller cabinet . The 480V feed also has a lockable disconnect and is located by the controller cabinet . The controller cabinet is marked " Caution Two Sources of Power " . We started to do this as we see this as being safer since we can troubleshoot the control circuit without 480V present ( No need for arc Flash Gear ) . A supervisor has a problem because he thinks that one disconnect should isolate all the power on the stand . Just looking for some opinions on this set-up .