texie
Senior Member
- Location
- Fort Collins, Colorado
- Occupation
- Electrician, Contractor, Inspector
If the existing meter is a meter main combo then it will have a permanently bonded neutral making it rated suitable ONLY for use as service equipment. As such it can not be left in place in what is now a feeder as this will violate 250.24(A)(5).