If you have two or more ground rods, Do you bring each condutor back to a commmon point or do you connect them together in series and just bring on connection back?:
IMO, it is easier to come out once and run the conductor long enough to loop to each rod. You can go to one rod then use a bonding jumper to the next rod but that uses 3 clamps and more room for error.If you have two or more ground rods, Do you bring each condutor back to a commmon point or do you connect them together in series and just bring on connection back?:
We are required by the power company to run a continuese ground conductor from rod #1 to rod#2.
Is that written in their terms of service or just what they expect?
Do they let you land the GEC in the meter? Ours doesn't.We are required by the power company to run a continuese ground conductor from rod #1 to rod#2.
Do they let you land the GEC in the meter? Ours doesn't.![]()
Still no conecction to meter,"not accesable" Defeating the purpose of grounding/bonding.
Rather than the meter bonded to the neutral,egc to rods.More direct. Why make lightning come into your service?
