Hello,
This is my first inquiry on your site and would like your opinions on a grounding issue that doesn't seem to be clearly defined by the NEC or our AHJ.
We have two seperate (same source MSB) 120/208 3P/4W panelboards feeding 3P/208V rectifiers (no neutral) through a single 2" EMT conduit (via a j box). What are your thoughts on the grounding conductors required in this conduit? I am arguing for one but the inspector indicated there should be grounding from each source panel.
Thanks for your time.
This is my first inquiry on your site and would like your opinions on a grounding issue that doesn't seem to be clearly defined by the NEC or our AHJ.
We have two seperate (same source MSB) 120/208 3P/4W panelboards feeding 3P/208V rectifiers (no neutral) through a single 2" EMT conduit (via a j box). What are your thoughts on the grounding conductors required in this conduit? I am arguing for one but the inspector indicated there should be grounding from each source panel.