jdelectricsvc
Member
We're located in "hickville," Iowa, so we don't receive many service calls for outdoor hottubs. On this rare occasion, the customer called and stated they needed a 240V 60A Siemens breaker. The original breaker was already taken out of the sub-panel...new one installed but I noticed the load neutral was installed on the neutral bar. Thinking this wasn't right I put the load neutral on the breaker and the pigtale on the neutral bar, but it instantly tripped and wouldn't reset. The hottub was still under warranty so I told the customer that there was still a problem and I wans't going to void their warranty by opening the hottub up. The technician shows up and says both neutrals must be on the neutral bar. Low and behold......it works, but can someone please give a clear reason behind not having a load neutral installed on the GFCI breaker and just installing the "line" pigtale neutral of the breaker to neutral bar? This sorts of defies the logic behind having the GFCI breaker. I furnished the new breaker, but because I installed the new breaker incorrectly and had to have the service tech come back how do you charge, if at all for the second service call...chalk it up to being taught something new and forget it.........