Marc, You are correct. It was my "bad" the lug was non compliant on the terminal and I should have posted that. But thinking about this install what good is the gfic breaker? Their is no neutral
A 2-pole GFCI breaker doesn't need a neutral to function. If there's any imbalance that isn't accounted for by analyzing both legs along with something possible on the neutral, it must be going to ground or a person. Doesn't need a neutral to trip.ceb said:. But thinking about this install what good is the gfic breaker? Their is no neutral
RUWIREDRITE said:nuisance tripping the Gfci because the ground was under sized. They really dont like an undersized ground.
RUWIREDRITE said:There tub technology must sense ground sizing i figure.
Dennis Alwon said:Or perhaps whoever skinned the NM cable cut a little to deep and nicked one of the wires.
RUWIREDRITE said:If the ground size isn't an issue as stated how come you can trip a gfci by touching the ground and neutral together on the load side of a gfci. I think its monitoring the ground also, and impedance can be an issue.
JohnJ0906 said:No it monitors the hot (s) and neutral, not the ground.
Dennis Alwon said:If a Gfci won't trip without a ground why would it trip if an undersized ground were there.