kwired
Electron manager
- NE Nebraska
- EC
I am pretty sure Beseoker can build you one if you needed it.Are there 2 phase VFDs available?![]()
No they can't make customer change out the panels, but what is to stop them from continuing to supply two phase service, or add on fees that make it more desirable to the customer to want to make some changes? Customer can always find a way to derive two phase if they want to utilize it.They can't make the customers change out the old 2Ø, 5W lighting panels (even though the customer really should!). Peco jumps at the chance to get rid of old phase changers though, whenever someone applies for new service.
I was recently commissioned to survey an old factory in North Philly where the old 2300V, 2Ø service had been upgraded to 13.2 kV, 3Ø. The customer owned his own primary distribution so there was access to the old equipment. Here are some pictures I took with my phone. (Don't worry, it was all de-energized.)
This is the 13.2 kV to 2300 V phase changer in a vault with a bunch of other dead oil pots.
Here's a vault with the two banks of old 2300V to 120/240V 2Ø oil-filled transformers. Note the 3-pole oil switches on the primaries. Don't be fooled! it really was 2Ø.
On the load side of these old pots was a bunch of 4-pole switches like these. (I-T-E was quite popular in Philly, back in the day!)
The I-T-E Imperial Corp.(purchased in 1976 by Gould Inc.) was headquartered in Spring House, PA, which I suspect is a Philadelphia suburb.