Only after the 2002 NEC. Before that, it was a ungrounded color.
I was told by a member of an NEC code panel that the only reason grey was ever allowed as a neutral color is the old black rubber insulation from way back would be painted white. When it soaked into the rubber it turned a grey finish and therefore the color was codified.
Strangely enough, I run across these every once in a while and they are still working whereas the new ones I put in seem to only last a year.
There is another way of looking at that: Are these vintage gfcis "still protecting"/effective or are they simply "working"?
Current generation GFCIs test themselves and lockout automatically when they fail- these old guys don't.
There could be something in your sitch (lightning will do it and you are in Florida.....) that is messing w/ the electronics-----the theory being GFCI locks itself after an event. That said, IME, newer GFCIs tend to trip /c of a surge but usually still work.
Last one of those I replaced was miswired all kinds of wrong and when I wired in the new GFCI, it locked out. those old ones will still pass power even if line and load are reversed, and I've seen them "trip" and keep downstream receptacles energized.
Just a caveat to anyone replacing GFCI that old: verify the line and load are correct, do not assume the previous ec got it right.
Don't assume line and load are on same position on the device as the new one either. Though new ones should not reset if you do get it wrong.