two pole breaker terminal size

Status
Not open for further replies.

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
I replaced a 40 year old ITE panel with a new Siemens. The AL wire for the electric furnace would not fit in the new 60 amp breaker. I noticed the ITE breaker was marked 2-6 and the new Siemens breaker was 4-6.

Anyone know why the change? This required using Polaris connectors to reduce the wire so it would fit in the new breaker.
 
Here is a blow up.

You torque 6-4 to 45 in/lbs and 3-2/0 to 50 in/lbs. Hence, wires from 6-2/0 will fit.

View attachment 18409
You sure that is a 60 amp breaker?

I don't use a lot of Siemens, but have had many motor or air conditioning applications where using 8 or even 10 AWG on 60 amp breakers - that one doesn't claim to be suitable for that small of a conductor. I can't recall ever seeing a 60 amp miniature breaker that accepts more then about 2 AWG either. Most 80-125 amp breakers I have seen will accept up to about 2/0 though
 
You sure that is a 60 amp breaker?

I don't use a lot of Siemens, but have had many motor or air conditioning applications where using 8 or even 10 AWG on 60 amp breakers - that one doesn't claim to be suitable for that small of a conductor. I can't recall ever seeing a 60 amp miniature breaker that accepts more then about 2 AWG either. Most 80-125 amp breakers I have seen will accept up to about 2/0 though

Same link as above.

http://www.homedepot.com/p/Siemens-60-Amp-Double-Pole-Type-QP-Circuit-Breaker-Q260/100017724

•Accepts #8-#2/0 AWG Cu or or #8-#2/0 AWG Al Wire

It is a cut and paste of the 60A breaker shown.
 
Last edited:
different breaker

different breaker

We must be comparing different Siemens 60 amp breakers. The ones I have do not have that type of screw. The screw is for combination flat or those square drivers. The breaker in your photo uses a flat screw driver.
 
same breaker

same breaker

There must be some mix up at the factory. I have the same model breaker. The breaker has the smaller ports and is stamped on the front 8-4. I will check with supply house.
 
I replaced a 40 year old ITE panel with a new Siemens. The AL wire for the electric furnace would not fit in the new 60 amp breaker. I noticed the ITE breaker was marked 2-6 and the new Siemens breaker was 4-6.

Anyone know why the change? This required using Polaris connectors to reduce the wire so it would fit in the new breaker.
Is #6 60 amp Rated? If you protect a wire at 60 amps why would need a wire larger than #6

Sent from my SM-T350 using Tapatalk
 
I may be missing something, but why not use the appropriate breaker size for the wire and make sure the furnace breaker is the right size for the furnace?
 
I may be missing something, but why not use the appropriate breaker size for the wire and make sure the furnace breaker is the right size for the furnace?

What Is amperage required and distance to furnace?
The OP is dealing with existing conditions, we don't know why they are what they are and it doesn't really matter, he is questioning why Siemens changed the terminations in the design of the breaker. The OP already had the solution.