kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Just done some tests to see what happens with a 50 amp 2 pole QO GFCI (with neutral).Not having a grounded connection to verify any line/load imbalance, it would default to a trip.
Plug breaker onto bus, leave neutral pigtail disconnected - breaker does turn on with no load you can measure 240 volts on output lugs (with a low Z meter so there is current above 4-6 mA flowing when testing).
Pressing test button does nothing.
Move one low Z meter test lead to the neutral bus in the panel so there is "fault current" flowing and the breaker trips, even though the neutral to the breaker was not connected. (this surprised me a little)
Thought I might read some voltage between the unterminated neutral pigtail and the neutral bus, but did not. (pretty sure I still had meter on low Z setting)
Connected neutral pigtail to neutral bus and things worked as they should - test button did trip the breaker as well.
Can't tell you if other brands of GFCI's will do the same, guessing Homeline does do the same though.