bellington
Senior Member
- Location
- Hahira, GA
- Occupation
- Consultant
On an island with 5 buildings, 29 service panels, solar, battery, and diesel generator, providing 480 3-phase, and at least (3) 480/208 step-down transformers, are we saving a significant amount of money on equipment and wire by running 9 service panels on just 2 legs of 208?
For each of the (9) 2-leg 208 panel, what is the acceptable engineering terminology for labeling? They are functioning as single-phase, similar to 240. Should the drawings simply call them 120/240, 1 phase, 2 pole, 3 wire? Or, should they be labeled 120/208, 2 phase, 2 pole, 3 wire, even though the 2 phases functions as 1?
Are 208/480 step-up transformers a new fad? For a small island, wouldn't another set of 480 3-phase feed lines be significantly cheaper and more efficient than running 208 lines large enough to handle a 175 KVA step-up transformer and the cost of the transformer?
Thanks for any input you may provide.
For each of the (9) 2-leg 208 panel, what is the acceptable engineering terminology for labeling? They are functioning as single-phase, similar to 240. Should the drawings simply call them 120/240, 1 phase, 2 pole, 3 wire? Or, should they be labeled 120/208, 2 phase, 2 pole, 3 wire, even though the 2 phases functions as 1?
Are 208/480 step-up transformers a new fad? For a small island, wouldn't another set of 480 3-phase feed lines be significantly cheaper and more efficient than running 208 lines large enough to handle a 175 KVA step-up transformer and the cost of the transformer?
Thanks for any input you may provide.