Yes, the part about stepping down and back up again is my issue. The part about stepping down and back up again was the reason for this original 2 questions:
...
Are 208/480 step-up transformers a new fad? For a small island, wouldn't another set of 480 3-phase feed lines be significantly cheaper and more efficient than running 208 lines large enough to handle a 175 KVA step-up transformer and the cost of the transformer?
My initial take is:
You never save money by stepping down and back up again if you have a choice about both ends. Yes, it would make more sense to send 480 and only step down where you need to.
I'm still confused about the general design.
208/480 step up transformers are a thing because they allow connecting grid tied 480V inverters to 208V utility services. (The 'primary' should be the side connected to the utility so that makes it a 'step up'.) I don't see how they are an advantage when you're not dealing with a utility and have the available option to interconnect an inverter at 480. (Who suggested it was a good idea?)