For AC Cable330.40 Boxes and Fitting.
Fittings used for connecting Type MC cable to boxes, cabinets, or other equipment shall be listed and identified for such use.
320.40 Boxes and Fittings.
At all points where the armor of AC cable terminates, a fitting shall be provided to protect wires from abrasion, unless the design of the outlet boxes or fittings is such as to afford equivalent protection, and, in addition, an insulating bushing or its equivalent protection shall be provided between the conductors and the armor. The connector or clamp by which the Type AC cable is fastened to boxes or cabinets shall be of such design that the insulating bushing or its equivalent will be visible for inspection. Where change is made from Type AC cable to other cable or raceway wiring methods, a box, fitting, or conduit body shall be installed at junction points as required in 300.15.
Nope I am just long winded.Originally posted by roger:
Am I getting to be a little to concise?
FWIW, Arlington has some two-screw compression strap type dual-listed connectors that are OK for NM as well as MC/AC. The L15A single screw saddle connector is also listed for certain NM as well as MC/AC.Originally posted by hbiss:
Also, I hope you are not confusing NM two screw connectors with these.
Are you saying that with the connectors with a plastic throat on the end that you don`t use antishort bushings ????Originally posted by scott moran:
The "two screw" connectors you are talking about are not listed for greenfield or bx. They are rated for flexible cord usage in dry areas. The "one screw" connectors are what you are looking for. But you even have to watch those, based on the design you may need to use the anti-short bushings. These are also known as red heads.
Scott
Scott I do not know what you mean.Originally posted by scott moran:
The "two screw" connectors you are talking about are not listed for greenfield or bx. They are rated for flexible cord usage in dry areas. The "one screw" connectors are what you are looking for.
Hi Scott I believe you are under Chicago's code so what I say may not apply in your area.Originally posted by scott moran:
These are what are commonly called around here "take all". These are not at all what is accepted or generally used.............These are more commonly used for flexible cords. I am sure that they may be used for NM, but since NM is outlawed here we dont have to worry about that.
Bob,The three fittings I posted are not to be used with flexible cords or NM because they have reduced throats to be used with MC, AC, FMC and they are very common around here for those products.